Thread: Amperage Draw ...heater and pump
    Apr 2012
    Colorado
    Default Re: Amperage Draw ...heater and pump
    Try using your service utility meter. The electronic ones usually sends a pulse every 1Wh.
    Let me give you an example with an electronic service meter (how I measured my two speed pump usage):
    Everything off (baseline): 8pulses in 84seconds or 5.714pulses/second or 342.8W
    pump low: 11pulses in 73seconds = 9.041 pulses/second difference is 3.327pulses/second or 200W
    pump hi: 30pulses in 78seconds = 23.08 pulses/second diff 17.37pulses/second or 1042W
    Here you can also see that two speed pump uses 1/4 or less of the energy on low (half of full speed).
    To get an amperage reading, you can divide the power by the voltage, i.e. 1024W/230V = 4.45A. This assumes the power factor is one which is not always true, but should be close for motors, but it doesn't really matter because your utility company charges you for the energy used, not the current.
    When you do your readings, make sure anything else in your house will not be switched on/off (like fridges), since it will affect the accuracy of your readings.
    14' 1900gal intex AG -- hayward S166T filter -- hayward max-flow 1.16HP dual speed 12/27GPM -- intex SWC -- 120sqft sungrabber panels
    Jun 2012
    Wisconsin
    Not sure of your local regulations, but here it is a code violation to have ANY other electrical device on the same breaker/circuit as your pool pump. The requirement is in fact a twist lock plug so only one outlet is in the box.
    I'm an electrical engineer so I can help you with the current draw part...
    The motor can be wired for 120 or 240 volts. 115/230 is just a old fashion term, but pretty much all of north america is over 240 volts now for residential. The motor max amps is the cold starting amps required to turn the motor from a dead stop, this can be anywhere from 1.5-2 times the normal current. That being said, you have to size circuits based on that value so the fact it will draw less current means nothing.
    This motor at normal 120 volts will draw a maximum of 17.25 amps. If it is wired for 240 volts, then the maximum current will be 8.6 amps.
    The circuit breaker is WAY over sized for this motor, did a licensed electrician put this in?
    The circuit breaker for this motor should have been 20 amps, wired with 12 gauge wire, and again it should be in a water tight electrical box with a twist lock plug that only allows for 1 plug to be on the circuit.
    At my home for example, I have two separate feeds, one 20 amp circuit feeding my pool and another 20 amp circuit feeding a outdoor outlet that sits under my deck for anything I need to plug in on the deck.
    I wouldn't recommend doing this any other way.
    Regards.
    Gregg, we have the same code in my part of NJ. We have additional requirements about the max length of the pump cord as well, plus there must be an addition GFI 120v outlet within a certain distance of the pool.