    Default Re: HP6002 Heat Pump - High Pressure

    Have you had the unit serviced recently? Overcharging can cause this. The fact that it's kicking out in 5 seconds kind of leads me to believe what you have is a pressure switch failure.
    On any heat pump, the most common cause of high pressure is debris clogging the condenser. On a pool heat pump it may be called something else. Can you backwash, or reverse the flow through the heat pump? Have you had a filter failure that would allow gunk to get to it? Scale build-up will also reduce heat transfer, but wouldn't happen suddenly. It would start out by running several minutes, then cycling off and coming back on in a minute or two.
    Intex 15ftx4ft 4500 gal. 3/4 HP Pentair WhisperFlo pump. Hayward 21" sand filter. Taylor K-2006 & K-1106 kits. PF=27

  2. #2
    PoolDoc's Avatar
    PoolDoc is offline Administrator Quark Inspector PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars
    Join Date
    Jan 2005
    Location
    Georgia
    Posts
    11,207

    Default Re: HP6002 Heat Pump - High Pressure

    It may be a Hayward HeatPro, but I'm not sure.