    [QUOTE=The Raddish]
    What I have done is put in 3/4" conduit from the breaker box to a T-junction under the deck. The conduit is buried about 14" or so, which is deeper than the 12" required by 680.
    QUOTE]

    Is this an older version of 680? I'm looking at the 2005 version and it states 18" for nonmetallic raceways.

    I too only went about 14" down because my ground is loaded with rocks so I don't know if it will fly or not.

    Sorry about the duplicate response on bonding - I didn't see John Ts answer while I was writing mine.

    Peter

  2. #2
    NWMNMom is offline Registered+ Widget Weaver NWMNMom 0
    Join Date
    Nov 2004
    Location
    WAAAY NW Minnesota
    Posts
    461

    Default Re: AG Pool wiring and other headaches

    Ok, thanks for the answers. A couple of things:

    1) we can't move the pool anywhere else (but didn't have problems with bugs in our 18' round, so fingers crossed, we won't when putting this one in the same spot)
    2) we live 10 miles from the nearest town (if you can call it that - 20 miles from one that has anything nearing govening bodies that give permits) so permits are not an issue
    3) if a new panel is required closer we will put one in
    4) Ok, I'll talk to him about bonding too

    Thanks!

  3. #3
    Join Date
    Dec 2004
    Location
    Rocket City, AL, USA.
    Age
    51
    Posts
    117

    Default Re: AG Pool wiring and other headaches

    Quote Originally Posted by prh129
    Is this an older version of 680? I'm looking at the 2005 version and it states 18" for nonmetallic raceways.
    This is true if the breakers are not GFI. That aspect seems to make the difference. If your circuits are all GFI at the breaker box, then 12" is the required depth for nonmetallic raceways. If they are not GFI at the breaker box, then 18" is required.

    At least, that is my understanding of the code.

  4. #4
    prh129 is offline Lifetime Member Widget Weaver prh129 0
    Join Date
    Mar 2006
    Location
    Rehoboth, MA
    Posts
    258

    Default Re: AG Pool wiring and other headaches

    Quote Originally Posted by The Raddish
    This is true if the breakers are not GFI. That aspect seems to make the difference. If your circuits are all GFI at the breaker box, then 12" is the required depth for nonmetallic raceways. If they are not GFI at the breaker box, then 18" is required.

    At least, that is my understanding of the code.
    OK - I see where that is defined in section 300.5. I will have a GFI breaker on the circuit so I would be covered in that case with a 12" depth but I'm not sure it meets with part 680.10.

    It is not clear to me if the depths listed in 680.10 apply only to non-pool wiring that can't be moved away from the pool area or if it's for all wiring in the pool area. I'd like to know up front in case it becomes an issue at inspection time.

    John T - you seem to have experience with this - what do you know about this?

    Thanks

    Peter

  5. #5
    Join Date
    Dec 2004
    Location
    Rocket City, AL, USA.
    Age
    51
    Posts
    117

    Default Pulling wire through conduit...

    ...any tricks?

    I'm pulling three 10AWG and six 12AWG wires through about 30 feet of 3/4" nonmetallic conduit with two 90º standard radius turns.

    I do have string strung through the conduit, so I can tie it off if needed.

  6. #6
    Join Date
    Dec 2004
    Location
    Indiana.
    Posts
    700

    Default Re: AG Pool wiring and other headaches

    Quote Originally Posted by prh129
    OK - I see where that is defined in section 300.5. I will have a GFI breaker on the circuit so I would be covered in that case with a 12" depth but I'm not sure it meets with part 680.10.

    It is not clear to me if the depths listed in 680.10 apply only to non-pool wiring that can't be moved away from the pool area or if it's for all wiring in the pool area. I'd like to know up front in case it becomes an issue at inspection time.

    John T - you seem to have experience with this - what do you know about this?

    Thanks

    Peter
    Peter, the first thing you need to be aware of is that local codes are often more strict than NEC, and sometimes have pretty unexpected requirements. Often, cities have a handout that outlines local codes. Also be aware that there are changes regarding pools in every revision of the NEC, and 2005 had many. These changes are mostly clarifications, because this stuff is confusing, and many electricians and inspectors don't understand it. Even if you are NEC 2005 to the letter, you may not be in compliance with local codes.

    680 says no wiring with 5ft of the inside of the pool wall except for pool equipment feeds unless space or property lines make it necessary. For pool equipment wiring, 6 inches is the required depth for metal conduit, and 18 inches for non-metallic conduit. 680 does not make the exception for GFI. Although your 12 inch depth may meet article 300, it is in violation of 680.

    It is my understanding that this requirement applies to all wiring in the pool area, even if it is not pool related and allowed by the space exception. Also, utility companies do not conform to NEC, but rather have their own code (NESC). If this affects you, contact your power company.

    In a comment above, another poster stated that you shouldn't bond a double insulated pump motor. Per NEC 2005, the bonding wire must be installed, just not connected to the motor in the event a replacement motor is installed that requires bonding. These are primarily above ground pumps.

+ Reply to Thread

Similar Threads

  1. New house, new pool, new headaches.
    By jcgeorge in forum Pool Startup, Shutdown, & Winter Operation
    Replies: 1
    Last Post: 07-27-2012, 04:18 PM
  2. Tips on removing pool light wiring from conduit??
    By imamachine in forum In-Ground Pool Construction and Repair
    Replies: 2
    Last Post: 06-20-2012, 07:18 PM
  3. Too much chlorine, headaches, nausea
    By mida68 in forum Salt Generators (SWCG) & other Chlorine Feeders
    Replies: 3
    Last Post: 04-01-2007, 08:39 PM
  4. wiring for a heat pump(new IG pool)question
    By freddyttt in forum Pool Equipment & Operations
    Replies: 5
    Last Post: 09-08-2006, 01:01 PM
  5. Pool Heater Wiring Issue
    By TexasPoolGuy in forum Pool Equipment & Operations
    Replies: 2
    Last Post: 08-01-2006, 01:32 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts