Re: How much water flow at low speed?
Thanks for all the responses. While there seems to be some discussion regarding the actual GPM I should be expecting and what the electricity savings would be -- it does seem to confirm that what I am seeing is not right.
From information on Jandy's reference sheet (http://www.jandy-downloads.com/pdfs/pumprefguide.pdf), my SHPM 2.5-2 should provide roughly 160 GPM at 40' of head (high speed using 11 amps), and 80 GPM at 10' of head (low speed using 4 amps). I have no idea what my head is, but those numbers seem like they might be consistent with each other for comparison (and follow Richard's comment). If the 4 amps vs. 11 amps (from the Jandy chart) seem right, it isn't quite the one-sixth Richard was talking about, but could still provide some energy savings to run twice as long on low speed. 27% savings from current usage I guess ((11 amps - 2 times as long * 4 amps) / 11 amps).
Jason
-
Re: How much water flow at low speed?
That is correct and prettyr typical of two speed pumps. The energy consumption is usually about 1/3 of high speed but you have to run twice as long so the effective energy consumption is 2/3 or about 1/3 savings. Different pumps will vary slight about this number but they are all pretty close.
By the way, if you look at any two speed pump head curve, you can actually prove the pump affinity equations. The example you gave has 1/2 the GPM at 1/4 the head which is exactly what the affinity equations predict. The entire low speed curve is simply a scaled version of the high speed curve.
Last edited by mas985; 09-02-2007 at 12:36 PM.