Re: Bypass Valve On Heater
Regular PVC does tend to start to soften above 90 degrees. If a spa is being heated, the water will regularly be above 100 degrees. Since there are so many different Mini-Max models, some with bulkhead fittings, some with cast metal headers, a good recommendation is to use a short section of CPVC on the inlet and outlet ports. I always do this on my heater installations and have never had an issue with the connections directly at the heater unless there is a malfunction in the heater itself. A couple of short pieces of CPVC (6"-12") does not cost much and is, in my opinion, worth the extra cost and effort.
Unless you have a "fireman's" switch on your timer (for heating a pool) or an auto control with a cool-down cycle, most people will not cool their heaters properly after using them, especially with spa use. Even the retained heat in a newer heater and plumbing will eventually warp the systems plumbing if not cooled. Heater manufacturers say that proper cool-down can add 50% to the life of a pool/spa heater.
Just Thursday had to re-plumb a system that was only 4 years old but had very regular spa use. It is a manually-controlled system and the customer said he was never told about cooling the system before shutting the pump down
Just my experience.
-
Re: Bypass Valve On Heater
Here are one set of pressure deratings for both PVC and CPVC. 2" schedule 40 PVC has a rating of 200 PSI at 110 deg F which much more than what is needed for a typical pool system.
It is true that PVC is more easily deformed at higher temperatures but according to this reference, PVC really doesn't start to significantly soften until 54 degrees C or 129 degrees F and that is with a lot of loading. The derating for pressure drops much sooner but the rigidity isn't affected as quickly unless of course there is a large load on the pipe but given the short sections of pipe, it is unlikely that the pipe would ever sag.
From my personal experience, I have never had a problem with heat deformation of the pipe exiting my heater. I also have had experience bending PVC pipe with a heat gun and you have to get it much hotter than what a heater could do before it even starts to bend.
Last edited by mas985; 04-05-2009 at 04:02 PM.