Thread: Electrical Terminology & Safety Tips

Hybrid View

  1. #1
    sturev's Avatar
    sturev is offline Registered+ Thread Analyst sturev 0
    Join Date
    May 2010
    Posts
    87

    Default Re: Electrical Safety Tips

    Have you heard of bonding non electrical components? I have a hydralic pump in my pool (counter current swim machine), and while there's no power to it, they wanted it bonded to the metal frame of the pool, and then they wanted the pool frame bonded to all the other componets (pump, heater, etc)... There's even a stainless steel handle on the swim machine (it's attached to plastic, not touching any other metal), and they wanted that bonded to the rest of the system...? BTW, the hydralic lines are rubber of course... Any thoughts on that?
    Evan S.

    AG FastLane Pool, 9x13 ~ 3,000 gal, COVERED/INSULATED 23X7, 30 gpm water pump (runs 12 hrs a day) AND a Hayward Power-Flo LX 1.5 hp Pump (only used on occasion for the pool sweep), Hayward 100K BTU Heater, Waterway Flo-Pro Skim Filter & Slime Bag, no other filters

  2. #2
    Poconos is offline SuperMod Emeritus Whizbang Spinner Poconos 4 stars Poconos 4 stars Poconos 4 stars Poconos 4 stars Poconos 4 stars Poconos 4 stars
    Join Date
    Dec 1969
    Location
    Honesdale PA
    Posts
    1,802

    Default Re: Electrical Safety Tips

    I'm one that believes in common sense and have trouble with some codes. Just ask CarlD. Can't say I ever dug into grounding codes and initially it may not make sense to tie non-electrical components together but......considering pool water is a conductor of electricity and it doesn't take much current to zap somebody and pool water is in contact with electrical components somewhere in the system, maybe it does make sense. I can't say one way or another.
    Al
    16'x32' oval 22K gal IG vinyl pool; ; Hayward S244T sand filter; Hayward superpump 1 HP pump; hrs; K-2006; PF:5.5

  3. #3
    CarlD's Avatar
    CarlD is offline SuperMod Emeritus Vortex Adjuster CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars
    Join Date
    Dec 1969
    Location
    North Central NJ
    Posts
    6,571

    Default Re: Electrical Safety Tips

    In my town EVERYTHING metal must be bonded--unless it's not attached, like a solar reel.

    But my ladder, my drop-in steps handrails, the pool structure, cross members ALL had to be bonded, as well as, of course, the pump.

    Codes don't always make sense but they always must be obeyed to the inspector's satisfaction (!).

    Insurance companies won't pay a claim if you needed a building permit and didn't get one. It's as simple as that. If you have an "outlaw" pool and someone gets hurt, Ol' Indemnity Plus will let you swing in the breeze.
    Carl

  4. #4
    Join Date
    May 2010
    Location
    Arizona
    Posts
    249

    Default Re: Electrical Safety Tips

    The main idea is to ground all the various components of your pool together with copper wires. You can use Bare or insulated wires, and somewhere there could be a code dictating a wire size, but in my mind, all these grounding wires need to be grounded directly to the GFCI ground wire or the (Green) Grounding screw. Twist them together, use wire nuts, crimp them together, even solder them, but the "Final Run" goes back to the GFCI.
    Last edited by BigTallGuy; 06-19-2010 at 12:40 AM.
    If you can afford a swimming pool and computer, you can probably afford to help keep the PoolForum alive. Please be a responsible member and subscribe today. You'll probably save more than the membership fee on your first trip to the pool store. BTG

  5. #5
    Ohm_Boy is offline Registered+ Thread Analyst Ohm_Boy 0
    Join Date
    Dec 2004
    Location
    .
    Posts
    63

    Default Re: Electrical Safety Tips

    Bonding and grounding are often confusing subjects, and are not the same.

    Bonding refers to connecting items together. All metal objects which can come into contact with pool water should be bonded together. This prevents any one of them from becoming a different potential from any other, from whatever influence, direct electrical contact, induced current, chemical, etc. This bonding prevents any current flow through the water itself, thereby protecting the occupants.

    Grounding, on the other hand, indicates a connection of one or more components to the service ground, equipment ground, ground rod, or other ground-potential reference point. Technically, there should only be one ground reference in an electrical installation, and that is most often at the service feed point. Everything else which is to be grounded should tie directly to that point with minimum resistance.

    Technically, in a grounded system, bonding is simply a means of connecting the ground wires to everything. In an ungrounded system, a bond wire just connects it all.

    There is also much debate over whether or not a bonded pool grid is to be grounded, and as I understand it, there are differing local code requirements as well. Some say ground, some say isolate. I'm personally a "ground it" fan.

    As an aside, the GFCI protected circuit does not need a ground connection to the GFCI to be protected. GFCI devices are designed to measure differential currents between the hot and neutral conductors, and open the circuit if that difference exceeds the trigger, around 5 milliamps. It is assumed that any difference in current is being diverted out-of-circuit by a body somewhere. Naturally, a ground is required by the circuit according to code, but it is not necessary for the GFCI feature to function.

  6. #6
    Join Date
    May 2010
    Location
    Arizona
    Posts
    249

    Default Re: Electrical Safety Tips

    Quote Originally Posted by Ohm_Boy View Post
    As an aside, the GFCI protected circuit does not need a ground connection to the GFCI to be protected. GFCI devices are designed to measure differential currents between the hot and neutral conductors, and open the circuit if that difference exceeds the trigger, around 5 milliamps. It is assumed that any difference in current is being diverted out-of-circuit by a body somewhere. Naturally, a ground is required by the circuit according to code, but it is not necessary for the GFCI feature to function.
    O.K. I bonded My pump motor and SWCG control unit together and ran the Bonding wire to the ground of the GFCI, if current from any source (say a bad extension cord as a bad example) was to somehow enter the Bonding/Grounding wire wouldn't that trip the GFCI? Or Does the GFCI only measure the currents between its own conductors?
    If you can afford a swimming pool and computer, you can probably afford to help keep the PoolForum alive. Please be a responsible member and subscribe today. You'll probably save more than the membership fee on your first trip to the pool store. BTG

  7. #7
    PoolDoc's Avatar
    PoolDoc is offline Administrator Quark Inspector PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars
    Join Date
    Jan 2005
    Location
    Georgia
    Posts
    11,207

    Default Re: Electrical Safety Tips

    Just wanted to jump in here, because this is a critical subject, and some of the answers may not stand out to people.

    1. Bonding and GFCI's protect people,
    not equipment.

    2. Breakers and fuses protect equipment.
    People not so much, except indirectly by preventing fires.

    3. Licensed electricians are better than unlicensed ones . . . usually,
    but in my experience, many licensed electricians, and some inspectors, are clueless around pools.

    4. To fully protect people, you should BOND every fixed piece of metal a wet swimmer could touch.
    (Codes may require more or less than this. You should obey electrical codes, too. At least, most of the time. Or if you are going to be inspected. )

    5. Codes sometimes allow discontinuous bonding via the rebar mat. This is NOT a good idea.
    Sometimes what was a continuous electrical connection in the mat becomes discontinuous. Use a full length bare copper wire, from start to finish.

    6. Codes sometimes allow conduit grounding. This is another bad idea, around pools.
    Conduits get disconnected: been there, got the shock, cussed out the electrician. Fortunately, did not die! Use a continuous wire ground around pools.

    7. All bonding mats are "grounded" intrinsically.
    But, if you ground to the box, you can get currents going. I don't like unplanned currents around pools. So, if you 'ground' your bond wires to the box, use a BIG wire for the bond and a SMALLER one for the ground-to-the-box connection. There are obscure electrical reasons for doing this. By the way, if your pump is correctly wired AND bonded, your bonding system will ALWAYS be connected to your ground system. (Unless you are using conduit grounding -- see below.)

    8. Grounding your 'bond' system to your box or panel can prevent weird corrosion issues.
    Again, not gonna explain this. But it's much better to prevent these sorts of issues than figure them out.

    9. Make FRICKING sure that you have a CONTINUOUS wire ground from your local wire panel back to your main distribution panel.
    Code may not require this, but you should. Again, got the shocks on this one. No, I do NOT like conduit grounds. Ever. Except maybe in the dry desert. Not near pools. Not in wet restaurant kitchens (where I got fried, while working as a plumber.) Maybe where nothing but camels and horny toads live. Or, maybe not even there.

    10. Shocks and wet people who want to keep living don't go together.
    Electricity can usually find an easier path to follow, than through a dry person with shoes on. Electricity can usually NOT find an easier path to follow than a wet nearly naked person. You have to work specially hard around pools to make sure that the easiest path is not through you, your family or friends!

    11. Think about the drips!
    And, I don't mean the jerks who become your close friend right about the time your pool is being finished. I've seen a lifeguard get a bad shock because they 'dripped' into a GFCI protected receptacle that was mounted horizontally, rather than vertically.

    12. Speaking of GFCI's, they fail around pools. A lot.
    Sometimes they fail 'safe' tripping every time you look at them. Sometimes, they fail 'DANGEROUS', and won't trip when you try to weld your extension cord to your pool ladder. (Or, when a lifeguard drips into the receptacle!) Check yours today, and several times each season. There's a GOOD reason for that little red or yellow button on your GFCI.

    13. Do not bring electricity into the pool area from outside the pool area.
    OK, I confess. I'm the idiot who did this, with an extension cord. All those electrical safeties in your pool area don't mean squat if you drag electricity in from elsewhere. Not one of my brighter moments. Pay for a 20A receptacle off the pool panel, when you do the pool.

    14. Electrical boxes should not be closer than 12" to the dirt. Ever. No matter what the code allows. When you put electrical boxes in the dirt, or even that close to the dirt, they WILL get wet and dirty. Probably not while there is still a warranty on the work, but soon after. Every SINGLE 'sealed' commercial pool light junction box I've ever opened was full of water. In fact, "sealed" electrical boxes seem to be much better at keeping water in, than at keeping it out.

    Hm-m-mh, that's all that comes to mind, right now.

    Ben
    "PoolDoc"
    Last edited by PoolDoc; 06-29-2010 at 08:15 AM. Reason: Thought of some more points to add. This is getting long.