Call Hayward to be sure, but a 40A circuit would be fine . . . IF you don't have a long run. Actually, what Hayward may be pushing you toward is a 40A breaker, with #6 wire. Wire length from the mains to pool equipment tends to be long, and voltage drops can cause problems. Larger wires avoid the problem.